Hi tengteng,
The horizontal piping in particular the suction line, of a split unit, requires a slope or slant towards the condensing unit. A simple rule to follow is 1 inch slope per 1 meter. Thats 7 inches slope for a 7 meter lenght of horizontal piping. That is to ensure gravity flow of oil most especially in the suction line wherein oil and refrigerant does not mix properly. Furthermore, Oil-trap must be at the bottom of the suction riser.
Chillz
Hi mga Bro i hope i'm nat late on this discussion, seem everyone has a good aswer but just to add to this matter I've attach a document to support thank and GOD Bless
Janew Jain said:Hi tengteng,
The horizontal piping in particular the suction line, of a split unit, requires a slope or slant towards the condensing unit. A simple rule to follow is 1 inch slope per 1 meter. Thats 7 inches slope for a 7 meter lenght of horizontal piping. That is to ensure gravity flow of oil most especially in the suction line wherein oil and refrigerant does not mix properly. Furthermore, Oil-trap must be at the bottom of the suction riser.