Ask ko lng sana kung paano kunin ang actual Kw/Ton ng isang Carrier condenser namin, Model # 38AH-028-611AA. Natanong lang ako ng boss ko.

Ang Actual parameters ko ay mga sumusunod:

FLA - 36.5
Voltage - 472/474/473

Mabuhay ang network natin! Salamat Po.

Reply to This

Replies to This Discussion

Mr.Lucky Chan e2 ang pagkakaalam ko 1 watt =3.414368btu/hr 1 kilowatt = 1.34 horsepower ikaw na bahala mag compute yan na ang basehan . hope it will help you! ayon sa data mo kc carrier unit 38000 btu/hr yan more or less 3 ton yan

Reply to This

Hello Laki Tian...

Play with this formulas:

KW/ton = 12 / EER
KW/ton = 12 / (COP x 3.412)
COP = EER / 3.412
COP = 12 / (KW/ton) / 3.412
EER = 12 / KW/ton
EER = COP x 3.412

If chillers efficiency is rated at 1 KW/ton,

COP = 3.5
EER = 12

The term kW/ton is commonly used for larger commercial and industrial air-conditioning, heat pump and refrigeration systems.

The term is defined as the ratio of energy consumption in kW to the rate of heat removal in tons at the rated condition. The lower the kW/ton the more efficient the system.

kW/ton = Pc / Er (1)

where

Pc = energy consumption (kW)

Er = heat removed (ton)

Reply to This

Try mo rin gamitin Power Converter Tool sa Homepage

Reply to This

Using the attached Carrier Data ( page 3 )consider this value:
KW/ton = 12 / EER
= 12/ 11.2
KW/ton = 1.07

Chillerman said:
Hello Laki Tian...

Play with this formulas:

KW/ton = 12 / EER
KW/ton = 12 / (COP x 3.412)
COP = EER / 3.412
COP = 12 / (KW/ton) / 3.412
EER = 12 / KW/ton
EER = COP x 3.412

If chillers efficiency is rated at 1 KW/ton,

COP = 3.5
EER = 12

The term kW/ton is commonly used for larger commercial and industrial air-conditioning, heat pump and refrigeration systems.

The term is defined as the ratio of energy consumption in kW to the rate of heat removal in tons at the rated condition. The lower the kW/ton the more efficient the system.

kW/ton = Pc / Er (1)

where

Pc = energy consumption (kW)

Er = heat removed (ton)
Attachments:

Reply to This

hELLO, i HOPE DI PA LATE ang reply ko,

your unit is air cooled condensing unit with nominal capacity of 25tons with 460v/3ph/60hz supply. H means high efficiency air cooled condensing units ( as per model).

The 1.07 kw/ton is the kw/ton if the unit is brand new or a factory test results.

My approach is get the input kw from the actual amps, voltage (ave), apply the sq root of 3 and the actual power factor. You have to do some math to get the input kw.

After you get the input kw, divide it by the actual cooling capacity. you can get the actual cooling capacity by using a testing machine, otherwise, you can use the factory supplied data which is 290000 Btuh or 24.167 tons.

You should get a little bit higher than 1.07 kw/ton

One suggestion, if you're boss was asking for kw/ton of the condensing unit, you better suggest to him to include the indoor unit (AHU) in computing for the actual kw/ton because a/c units (AHU & ACCU) are working together as a system. You can't evaluate it accurately if you only look on the ACCU alone. It should come together as a system.


Hope this will help.

Reply to This

Reply to This

RSS

To download books, reference manuals and softwares, movies and many more, just proceed to download center.

To advertise on this network, just proceed to our Buy from 2CO counter.

2CheckOut.com Inc. (Ohio, USA) is an authorized retailer for goods and services provided by HVAC Philippines. Contact Chillerman for details.

Forum

james russel san agustin

polising my hvac skillss 2 Replies

Started by james russel san agustin. Last reply by juddin E Garciso 8 hours ago.

Nestor Molato

??Procedures on Start up and Commissioning of Bitzer Screw Compressor CSH8561-125Y?? 6 Replies

Started by Nestor Molato. Last reply by Nestor Molato 9 hours ago.

© 2010   Created by Chillerman

Badges  |  Report an Issue  |  Privacy  |  Terms of Service

Sign in to chat!